When I had a Bluebird and drove coaches for FEMA (Coachman) I was always told to never start Gen. when plugged in to shore power.Why and is it the same with my Barth? Thank you. | ||
|
2/16 Captain Doom |
There should be a cutover relay that powers the coach from one or the other; this also disconnects shore power when the genset is under load, preventing back feed. Rusty "StaRV II" '94 28' Breakaway: MilSpec AMG 6.5L TD 230HP Nelson and Chester, not-spoiled Golden Retrievers Sometimes I think we're alone in the universe, and sometimes I think we're not. In either case the idea is quite staggering. - Arthur C. Clarke It was a woman who drove me to drink, and I've been searching thirty years to find her and thank her - W. C. Fields | |||
|
3/19 |
Because the Automatic Transfer Switch is likely to fail eventually, manually preventing two current inputs is prudent. Some of the Automatic Transfer Switches, such as Parallax ATS 100, were available with a thermal delay module as an added safety measure. My current coach is so complex that is has TWO ATS boxes, not just one. An idiosyncrasy of some, prior to the modern ATS 503, was that the relay points would bounce open if you were running your gen set while going down the road. No damage, just no more power to your roof AC or whatever. | |||
|
Official Barth Junkie |
My Regal has no automatic relay. There is a manual switch to choose either shore, genset, or off (neither). There is no way to get both sources at once. If you have this type of switch, you will have to manually switch over every time, but there is no way to harm either source. 9708-M0037-37MM-01 "98" Monarch 37 Spartan MM, 6 spd Allison Cummins 8.3 325+ hp | |||
|
Powered by Social Strata |
Please Wait. Your request is being processed... |